- Each Boiler (including EGB) is to be fitted with at least 1 safety v/v & where the water heating surface area is more than 46.5 m2,2 or more safety v/vs are to be provided. (Quick calculation of water heating surface area= π × D ×l× N (N= no of tubes)
- The safety v/v bore must be between 19mm-102mm
- Accumulation pressure test: with the steam stop v/v shut & the boiler burner firing continuously at full load capacity, the maximum pressure built up in the boiler should not exceed 6% of the maximumallowable working pressure. During this period feed water can only be admitted for safety reason only.
- The aggregate (total) relieving capacity of the safety v/v’s must not be less than the evaporating capacity of the boiler under maximum operating conditions.
- Each boiler safety v/v is to be fitted with an easing gear by which the safety v/v can be operated from a safe platform either by hand or by mechanical means.
- The area of the escape pipe has to be equal or greater than the combined outlet area of the two safety v/v’s. The pipe should be free of any restriction.
Hydrostatic pressure test Boiler pressure part (shell) 1.5 times ×M.A.W .P for 30 min Accumulation pressure test Safety v/v Should not exceed 6% M.A.W.P 2ND safety v/v setting 2nd safety v/v 3% more than previous v/v Main steam stop v/v test Main steam stop v/v 1.5 × x (where the v/v is xk 200) Water heating surface area , if more than 46.5 m2 , 2 safety v/v needed ,safety v/v bore must be between 19 to 102 mm. -