28/01/2020 at 17:12 #367
- Loss of Oil from Crankcase
– Operational leakage
– Foaming
– Suction pressure drops rapidly from evaporator
– Compressor running on high capacity (unloading setting)
Action
– Use defoaming agent during prolong shut down
– Shut stop valve in liquid supply line to expansion valve
– Suction and discharge valves to shut after shut-down
– Ensure unloading device in good working condition
– Install a suitable type or size expansion valve
- Excessive Loss of Oil Loss in Crankcase
– Overloading of oil separator
– Drop in crankcase pressure (foaming)
– Oil passing to the condenser and to the rest of the system
- Indication of Refrigerant Leakages
– Low refrigerant level in sight glass
– Large bubbles in sight glass
– Oil weeping at joint and connection
– Low suction pressure ( Relative lower pressure indicated across system)
– High superheat at compressor suction
– Compressor running continuously not maintaining room temperature
–
- Fall Off in Refrigerant Effect (Over a short period of time)
– Refrigeration loss thru shaft gland, pipes, fittings etc
– Broken suction or discharge valves
– Belt slipping
– Icing of expansion valve
- High Pressure Cut-out
– Insufficient or intermittent water flow for condenser cooling
– Scaled or fouled condenser
– Overcharging of refrigerant
- Low Pressure Cut-out, Short-cycling
– Evaporator coils heavily frosted
– Strainer chocked
– Leaky discharge valves
– Defective expansion valve
– Refrigerant undercharge
– Too cold inlet cooling water temperature
- Refrigerant Undercharged
– Large bubbles noted in sight glass
– Low suction & delivery pressure
– Continuous running of compressor-room temp not reducing
– Relative less frosting on compressor suction line/valve
– System performance drops –of course
shortage of refrigerant at the evaporator :
– Filter/Drier partially block
– Leakages
– Chocked filter for thermostatic expansion valve
– Incorrect type or wrong setting of expansion valve used
- Refrigerant Overcharged
– Sight glass refrigerant level higher than normal
– Higher HP/delivery pressure
– Compressor stopping on HP cutout
– Severe frosting on compressor suction line/valve
- Moisture in the System
– Frosting on inlet side of expansion valve
– Low suction pressure
– HOW moisture gets into the system ??
Actions
Renew drier
- Frost on Evaporator Coils
– Compressor runs longer
– Short cycling on LP switch
– Performance drops
– Low suction pressure –Refrigerant temperature drops to 0 degree Celsius or lower
- Compressor Drawing-in Refrigerant Liquid
– Excessive frosting at suction valve
– Oil level at compressor sump reduced
– High suction pressure
– Noisy compressor operation
- Noisy Compressor
– Liquid knock / hammering
– Lack of lubrication
– Internal components damaged
- Air in the System
– High condenser pressure (HP pressure)
– Jumping of pressure gauges pointer
– Compressor noisy
– Small bubbles at sight glass
– Relative small difference in SW in & out temperature –Less heat transfer
- Poor Cooling in Condenser
– Restricted cooling water
– High condenser pressure
– Incorrect temperature reading
– Water pump fault
– Choked strainer
– Dirty blocked tubes
– High SW temperature
-